ArduCounter: Unterschied zwischen den Versionen
(updated to the current version) |
Zeile 92: | Zeile 92: | ||
== Configuration of ArduCounter analog counters == | == Configuration of ArduCounter analog counters == | ||
This module and the corresponding sketch can be used to read out old analog ferraris energy counters. Therefore | This module and the corresponding sketch can be used to read out old analog ferraris energy counters. Therefore an ESP, Arduino Uno or Nano board needs to be connected to a reflection light barrier which consists simply of an infra red photo transistor (connected to A7 on Arduinos and A0 on ESP8266) and an infra red led (connected to D2 on Arduinos and to D6 on ESP8266), both with a resistor in line. The idea comes from Martin Kompf (https://www.kompf.de/tech/emeir.html) and has been adopted for ArduCounter to support old ferraris energy counters. | ||
To support this mode, the sketch has to be compiled with analogIR defined. | To support this mode, the sketch has to be compiled with analogIR defined. | ||
Zeile 160: | Zeile 160: | ||
This shows the measured values together with the frequency how often the individual value has been measured. It is obvious that most measurements result in values between 120 and 135, very few values are betweem 96 and 115 and another peak is around the value 95. | This shows the measured values together with the frequency how often the individual value has been measured. It is obvious that most measurements result in values between 120 and 135, very few values are betweem 96 and 115 and another peak is around the value 95. | ||
It means that the when the red mark of the ferraris disc is under the sensor, the value is around 95 and while the blank disc is under the sensor, the value is typically between 120 and 135. So a good upper threshold would be 120 and a good lower threshold would be for example 96. | It means that the when the red mark of the ferraris disc is under the sensor, the value is around 95 and while the blank disc is under the sensor, the value is typically between 120 and 135. So a good upper threshold would be 120 and a good lower threshold would be for example 96. | ||
== Get-Commands == | == Get-Commands == |
Version vom 8. Dezember 2019, 23:39 Uhr
ArduCounter | |
Count pulses, calculate time between pulses and convert this to readings for e.g. power consumption of Energy meters | |
Typ | Contrib |
Dokumentation | Thema |
Support (Forum) | Sonstiges |
Modulname | 98_ArduCounter.pm |
Ersteller | StefanStrobel (Forum / Wiki) |
This module implements an Interface to an Arduino or ESP8266 based counter for pulses on any input pin of an Arduino Uno, Nano, Jeenode, NodeMCU, Wemos D1 or similar device. The device connects to Fhem either through USB / serial or via tcp if an ESP board is used.
The typical use case is an S0-Interface on an energy meter or water meter, but also reflection light barriers to monitor old ferraris counters are supported
Counters are configured with attributes that define which Arduino pins should count pulses and in which intervals the Arduino board should report the current counts.
The Arduino sketch that works with this module uses pin change interrupts so it can efficiently count pulses on all available input pins. The module creates readings for pulse counts, consumption and optionally also a pin history with pulse lengths and gaps of the last pulses.
Availability
The module has been checked in to the FHEM svn. The corresponding arduino sketch can also be found under contrib in the subdirectory arduino/.
Prerequisites
This module requires an Arduino Uno, Nano, Jeenode, NodeMCU, Wemos D1 or similar device based on an Atmel 328p or ESP8266 running the ArduCounter sketch provided with this module
In order to flash an arduino board with the corresponding ArduCounter firmware from within Fhem, avrdude needs to be installed.
For old ferraris counters an Arduino Uno or Nano or ESP8266 board needs to be connected to a reflection light barrier which consists simply of an infra red photo transistor (connected to A7 on Arduinos and A0 on ESP8266) and an infra red led (connected to D2 on Arduinos and to D6 on ESP8266), both with a resistor in line.
This module also requires Device::SerialPort or Win32::SerialPort for communication via serial lines
define <name> ArduCounter <device>
or
define <name> ArduCounter <ip:port>
<device> specifies the serial port to communicate with the Arduino.
<ip:port> specifies the ip address and tcp port to communicate with an esp8266 where port is typically 80.
The name of the serial-device depends on your distribution. You can also specify a baudrate for serial connections if the device name contains the @ character, e.g.: /dev/ttyUSB0@38400. The default baudrate of the ArduCounter firmware is 38400 since Version 1.4
Examples:
define AC ArduCounter /dev/ttyUSB2@38400 define AC ArduCounter 192.168.1.134:80
Configuration of ArduCounter digital counters
Specify the pins where impulses should be counted e.g. as attr AC pinX falling pullup 30
The X in pinX can be an Arduino / ESP pin number with or without the letter D e.g. pin4, pinD5, pin6, pinD7 ...
After the pin you can use the keywords falling or rising to define if a logical one / 5V (rising) or a logical zero / 0V (falling) should be treated as pulse.
The optional keyword pullup activates the pullup resistor for the given Pin.
The last argument is also optional but recommended and specifies a minimal pulse length in milliseconds.
An energy meter with S0 interface is typically connected to GND and an input pin like D4. The S0 pulse then pulls the input to 0V. Since the minimal pulse lenght of the s0 interface is specified to be 30ms, the typical configuration for an s0 interface is attr AC pinX falling pullup 30
Specifying a minimal pulse length is recommended since it filters bouncing of reed contacts or other noise.
Example:
define AC ArduCounter /dev/ttyUSB2 attr AC pulsesPerKWh 1000 attr AC interval 60 300 attr AC pinD4 falling pullup 5 attr AC pinD5 falling pullup 30 attr AC verboseReadingsD5 attr AC pinD6 rising
This defines three counters connected to the pins D4, D5 and D5. D4 and D5 have their pullup resistors activated and the impulse draws the pins to zero. For D4 and D5 the arduino measures the time in milliseconds between the falling edge and the rising edge. If this time is longer than the specified 5 or 30 milliseconds then the impulse is counted. If the time is shorter then this impulse is regarded as noise and added to a separate reject counter.
verboseReadings5 causes the module to create additional readings like the pin history which shows length and gaps between the last pulses.
For pin D6 the arduino does not check pulse lengths and counts every time when the signal changes from 0 to 1.
The ArduCounter sketch which must be loaded on the Arduino or ESP implements this using pin change interrupts, so all avilable input pins can be used, not only the ones that support normal interrupts. The module has been tested with 14 inputs of an Arduino Uno counting in parallel and pulses as short as 3 milliseconds.
The configuration is then similar to the one for digital counters:
define ACF ArduCounter /dev/ttyUSB4 attr ACF analogThresholds 100 110 attr ACF flashCommand avrdude -p atmega328P -b57600 -c arduino -P [PORT] -D -U flash:w:[HEXFILE] 2>[LOGFILE] attr ACF interval 60 300 2 2 attr ACF pinA7 rising 20 attr ACF pulsesPerKWh 75 attr ACF stateFormat {sprintf("%.3f kW", ReadingsVal($name,"powerA7",0))}
To find out the right analog thresholds you can set devVerbose to 20 which will ask the firmware of your conting board to report every analog measurement. The ArduCounter module will count how often each value is reported and you can then query these analog level counts with get levels. After a few turns of the ferraris disc the result of get levels might look like this:
observed levels from analog input: 94: 21 95: 79 96: 6 97: 2 98: 3 99: 2 100: 2 101: 1 102: 3 105: 2 106: 1 108: 2 109: 1 110: 1 112: 1 113: 3 115: 4 116: 9 117: 14 118: 71 119: 103 120: 118 121: 155 122: 159 123: 143 124: 147 125: 158 126: 198 127: 249 128: 220 129: 230 130: 201 131: 140 132: 147 133: 153 134: 141 135: 119 136: 105 137: 109 138: 114 139: 83 140: 33 141: 14 142: 1
This shows the measured values together with the frequency how often the individual value has been measured. It is obvious that most measurements result in values between 120 and 135, very few values are betweem 96 and 115 and another peak is around the value 95. It means that the when the red mark of the ferraris disc is under the sensor, the value is around 95 and while the blank disc is under the sensor, the value is typically between 120 and 135. So a good upper threshold would be 120 and a good lower threshold would be for example 96.
Get-Commands
- info
- send a command to the Arduino board to get current counts.
- This is not needed for normal operation but might be useful sometimes for debugging.
- levels
- show the count for the measured levels if an analog pin is used to measure e.g. the red mark of a ferraris counter disc.
- This is useful for setting the thresholds for analog measurements.
- history
- shows details regarding all the level changes that the counter device (Arduino or ESP) has detected
- and how they were used (counted or rejected)
- If get history is issued with a pin name (e.g. get history D5) then only the history entries concerning D5 will be shown.
- This information is sent from the device to Fhem when it reports the current count but only if devVerbose is equal or greater than 5.
- The maximum number of lines that the Arducounter module stores in a ring buffer is defined by the attribute maxHist and defaults to 1000.
Set-Commands
- raw
- send the value to the board so you can directly talk to the sketch using its commands.
- flash
- flashes the ArduCounter firmware ArduCounter.hex from the fhem subdirectory FHEM/firmware onto the device.
- This command needs avrdude to be installed. The attribute flashCommand specidies how avrdude is called.
- If it is not modifed then the module sets it to avrdude -p atmega328P -c arduino -P [PORT] -D -U flash:w:[HEXFILE] 2>[LOGFILE]
- This setting should work for a standard installation and the placeholders are automatically replaced when the command is used.
- So normally there is no need to modify this attribute.
- Depending on your specific Arduino board however, you might need to insert -b 57600 in the flash Command.
- (e.g. for an Arduino Nano) ESP boards so far have to be fashed from the Arduino IDE. In a future version flashing over the air sould be supported.
- reset
- reopens the arduino device and sends a command to it which causes a reinitialize and reset of the counters. Then the module resends the attribute configuration / definition of the pins to the device.
- saveConfig
- stores the current interval, analog threshold and pin configuration to be stored in the EEPROM of the counter device
- so it can be retrieved after a reset.
- enable
- sets the attribute disable to 0
- disable
- sets the attribute disable to 1
- reconnect
- closes the tcp connection to an ESP based counter board that is conected via TCP/IP and reopen the connection
Supported readings
The module creates at least the following readings and events for each defined pin:
- pin.* e.g. pinD4
- the current internal count at this pin (internal to the Arduino / ESP device, starts at 0 when the device restarts).
- The name of this reading can be changed with the attribute readingNameCount[AD]?[0-9]+ where [AD]?[0-9]+ stands for the pin description e.g. D4
- long.* e.g. longD5
- long count which keeps on counting up after fhem restarts whereas the pin.* count is only a temporary internal count that starts at 0 when the arduino board starts.
- The name of this reading can be changed with the attribute readingNameLongCount[AD]?[0-9]+ where [AD]?[0-9]+ stands for the pin description e.g. D4
- interpolatedLong.*
- like long.* but when the Arduino restarts the potentially missed pulses are interpolated based on the pulse rate before the restart and after the restart.
- The name of this reading can be changed with the attribute readingNameInterpolatedCount[AD]?[0-9]+ where [AD]?[0-9]+ stands for the pin description e.g. D4
- calcCounter.*
- similar to long count which keeps on counting up after fhem restarts but this counter will take the pulses per kWh setting into the :calculation und thus not count pulses but real kWh (or some other unit that is applicable)
- The name of this reading can be changed with the attribute readingNameCalcCount[AD]?[0-9]+ where [AD]?[0-9]+ stands for the pin description e.g. D4
- reject.*
- counts rejected pulses that are shorter than the specified minimal pulse length.
- power.*
- the current calculated power at this pin.
- The name of this reading can be changed with the attribute readingNamePower[AD]?[0-9]+ where [AD]?[0-9]+ stands for the pin description e.g. D4
- pinHistory.*
- shows detailed information of the last pulses. This is only available when a minimal pulse length is specified for this pin. Also the total number of impulses recorded here is limited to 20 for all pins together. The output looks like -36/7:0C, -29/7:1G, -22/8:0C, -14/7:1G, -7/7:0C, 0/7:1G
- The first number is the relative time in milliseconds when the input level changed, followed by the length in milliseconds, the level and the internal action. -36/7:0C for example means that 36 milliseconds before the reporting started, the input changed to 0V, stayed there for 7 milliseconds and this was counted.
- countDiff.*
- delta of the current count to the last reported one. This is used together with timeDiff.* to calculate the power consumption.
- timeDiff.*
- time difference between the first pulse in the current observation interval and the last one. Used togehter with countDiff to calculate the power consumption.
- seq.*
- internal sequence number of the last report from the board to Fhem.
Attributes
- do_not_notify
- pin.*
- Define a pin of the Arduino board as input. This attribute expects either
rising
,falling
orchange
, followed by an optionalpullup
and an optional number as value. - If a number is specified, the arduino will track rising and falling edges of each impulse and measure the length of a pulse in milliseconds.
- The number specified here is the minimal length of a pulse and a pause before a pulse. If one is too small, the pulse is not counted but added to a separate reject counter.
- interval normal max min mincout
- Defines the parameters that affect the way counting and reporting works.
- This Attribute expects at least two and a maximum of four numbers as value.
- The first is the normal interval, the second the maximal interval, the third is a minimal interval and the fourth is a minimal pulse count.
- In the usual operation mode (when the normal interval is smaller than the maximum interval), the Arduino board just counts and remembers the time between the first impulse and the last impulse for each pin.
- After the normal interval is elapsed the Arduino board reports the count and time for those pins where impulses were encountered.
- This means that even though the normal interval might be 10 seconds, the reported time difference can be something different because it observed impulses as starting and ending point.
- The Power (e.g. for energy meters) is the calculated based of the counted impulses and the time between the first and the last impulse.
- For the next interval, the starting time will be the time of the last impulse in the previous reporting period and the time difference will be taken up to the last impulse before the reporting interval has elapsed.
- The second, third and fourth numbers (maximum, minimal interval and minimal count) exist for the special case when the pulse frequency is very low and the reporting time is comparatively short.
- For example if the normal interval (first number) is 60 seconds and the device counts only one impulse in 90 seconds, the the calculated power reading will jump up and down and will give ugly numbers.
- By adjusting the other numbers of this attribute this can be avoided.
- In case in the normal interval the observed impulses are encountered in a time difference that is smaller than the third number (minimal interval) or if the number of impulses counted is smaller than the fourth number (minimal count) then the reporting is delayed until the maximum interval has elapsed or the above conditions have changed after another normal interval.
- This way the counter will report a higher number of pulses counted and a larger time difference back to fhem.
- If this is seems too complicated and you prefer a simple and constant reporting interval, then you can set the normal interval and the mximum interval to the same number. This changes the operation mode of the counter to just count during this normal and maximum interval and report the count. In this case the reported time difference is always the reporting interval and not the measured time between the real impulses.
- factor
- Define a multiplicator for calculating the power from the impulse count and the time between the first and the last impulse.
- This attribute is outdated and unintuitive so you should avoid it.
- Instead you should specify the attribute pulsesPerKWh or readingPulsesPerKWh[0-9]+ (where [0-9]+ stands for the pin number).
- readingFactor[0-9]+
- Override the factor attribute for this individual pin.
- Just like the attribute factor, this is a rather cumbersome way to specify the pulses per kWh.
- Instaed it is advised to use the attribute pulsesPerKWh or readingPulsesPerKWh[0-9]+ (where [0-9]+ stands for the pin number).
- pulsesPerKWh
- specify the number of pulses that the meter is giving out per unit that sould be displayed (e.g. per kWh energy consumed). For many S0 counters this is 1000, for old ferraris counters this is 75 (rounds per kWh).
- Example: attr myCounter pulsesPerKWh 75
- readingPulsesPerKWh[0-9]+
- is the same as pulsesPerKWh but specified per pin individually in case you have multiple counters with different settings at the same time
- Example:
- attr myCounter readingPulsesPerKWhA7 75
- attr myCounter readingPulsesPerKWhD4 1000
- readingNameCount[0-9]+
- Change the name of the counter reading pinX to something more meaningful.
- readingNameLongCount[0-9]+
- Change the name of the counter reading longX to something more meaningful.
- readingNameInterpolatedCount[0-9]+
- Change the name of the counter reading InterpolatedLongX to something more meaningful.
- readingNameCalcCount[AD]?[0-9]+
- Change the name of the real unit counter reading CalcCounterX to something more meaningful.
- Example: attr myCounter readingNameCalcCountD4 CounterHaus_kWh
- readingNamePower[0-9]+
- Change the name of the power reading powerX to something more meaningful.
- readingStartTime[0-9]+
- Allow the reading time stamp to be set to the beginning of measuring intervals
- verboseReadings[0-9]+
- create additional readings: timeDiff, countDiff and lastMsg for each pin
- devVerbose
- set the verbose level in the counting board. This defaults to 0.
- If the value is >0, then the firmware will echo all commands sent to it by the Fhem module.
- If the value is >=5, then the firmware will report the pin history (assuming that the firmware has been compiled with this feature enabled)
- If the value is >=10, then the firmware will report every level change of a pin
- If the value is >=20, then the firmware will report every analog measurement (assuming that the firmware has been compiled with analog measurements for old ferraris counters or similar).
- maxHist
- specifies how many pin history lines hould be buffered for "get history".
- This attribute defaults to 1000.
- analogThresholds
- this Attribute is necessary when you use an arduino nano with connected reflection light barrier (photo transistor and led) to detect the red mark of an old ferraris energy counter. In this case the firmware uses an upper and lower threshold which can be set here.
- Example: attr myCounter analogThresholds 90 110
- In order to find out the right threshold values you can set devVerbose to 20, wait for several turns of the ferraris disc and then use get levels to see the typical measurements for the red mark and the blank disc.
- flashCommand
- sets the command to call avrdude and flash the onnected arduino with an updated hex file (by default it looks for ArduCounter.hex in the FHEM/firmware subdirectory.
- This attribute contains avrdude -p atmega328P -c arduino -P [PORT] -D -U flash:w:[HEXFILE] 2>[LOGFILE] by default.
- For an Arduino Nano based counter you should add -b 57600 e.g. between the -P and -D options.
- Example: attr myCounter flashCommand avrdude -p atmega328P -c arduino -b 57600 -P [PORT] -D -U flash:w:[HEXFILE] 2>[LOGFILE]
- keepAliveDelay
- defines an interval in which the module sends keepalive messages to a counter device that is conected via tcp.
- This attribute is ignored if the device is connected via serial port.
- If the device doesn't reply within a defined timeout then the module closes and tries to reopen the connection.
- The module tells the device when to expect the next keepalive message and the device will also close the tcp connection if it doesn't see a :keepalive message within the delay multiplied by 3
- The delay defaults to 10 seconds.
- Example: attr myCounter keepAliveDelay 30
- keepAliveTimeout
- defines the timeout when wainting for a keealive reply (see keepAliveDelay) The timeout defaults to 2 seconds.
- Example: attr myCounter keepAliveTimeout 3
- keepAliveRetries
- defines how often sending a keepalive is retried before the connection is closed and reopened.
- It defaults to 2.
- Example: attr myCounter keepAliveRetries 3
- nextOpenDelay
- defines the time that the module waits before retrying to open a disconnected tcp connection.
- This defaults to 60 seconds.
- Example: attr myCounter nextOpenDelay 20
- openTimeout
- defines the timeout after which tcp open gives up trying to establish a connection to the counter device. This timeout defaults to 3 seconds.
- Example: attr myCounter openTimeout 5
- silentReconnect
- if set to 1, then it will set the loglevel for "disconnected" and "reappeared" messages to 4 instead of 3
- Example: attr myCounter silentReconnect 1
- disable
- if set to 1 then the module closes the connection to a counter device.