Tecalor THZ Heatpump
German version: Tecalor THZ Wärmepumpe
This article describes how to connect to a Stiebel Eltron / Tecalor THZ/LWZ 303/304/404 heatpump and to read and write settings from and to the heating.
For better understanding: Tecalor is the end customer brand of Stiebel Eltron. In the following the system will be called "THZ"
Tested are Software Versions 4.09, 4.19, 4.39 and 5.39. Older versions may work but there's no guarantee for. NOTE: This manual is for persons who are familiar with electronics. The author and the developer are not liable for any damage and there's no warranty.
ATTENTION!! Since v0.087 the reading names have changed. To have intuitive and consistent reading names the readings names changed to sXXX and pXXXX for status values and parameters in the heating. See readings section for more information.
If you update you sure have to reconfigure readingsGroups, dashboards, and so...
Connection to the heatpump
Local via RS232 or USB
The THZ has two interface which can be used for a connection.
  • One serial interface behind the right door which can be used with a MNL-SG3 Plug
  • One USB interface on the electronics board which can be used with a TYPE-B USB cable.
Warning!!! The USB interface is on the back side of the electronics board behind the coverage wich is behind the right door. Do not connect the USB while the system is powered on! Before removing the coverage you have to power off the complete heatpump!!
The baud rates may vary based on hard- and software release between 9600 and 115200 for RS232. For USB it's always 115200 baud. More information how to connect to the heatpump with RS232 can be found here: Robert Penz Homepage
Remote connection with Ser2Net
If the FHEM server is not near the heatpump you can connect with Ser2Net. This will provide a virtual serial interface on a TCP-Port
Installation Ser2Net on Linux
To install Serial-Port-Server Ser2Net just follow these steps:
sudo apt-get install ser2net
in /etc/ser2net.conf (/dev/ttyXXX)
The port can be chosen on your own as long as it's still unused.
Tested Host-Systems
This module was tested on FritzBox, nas-qnap, Raspberry Pi and MacOS.
Definition in FHEM
Direct RS232 serial or USB
define Mythz THZ /dev/ttyUSB0@115200 # or (/dev/ttyXXX)
attr Mythz interval_sGlobal 300 # Internal Polling Interval 5min
attr Mythz interval_sHistory 28800 # Internal Polling Interval 8h
attr Mythz interval_sLast10errors 120 # Internal Polling Fault Memory
define FileLog_Mythz FileLog ./log/Mythz-%Y.log Mythz
If you don't define the attributes interval_sGlobal and interval_history (or they are 0), the internal polling is disabled. Sure you can also poll with the "at" command outside the module:
define atMythzFB at +*00:05:00 {fhem "get Mythz sGlobal","1";;return()}
define atMythz09 at +*08:00:00 {fhem "get Mythz sHistory","1";;return()}
Over network with Ser2Net
define Mythz THZ 192.168.0.244:2003
attr Mythz interval_sLast10errors 120 # Internal Polling Interval Fault Memory
If the connection to the heatpump was successful you should see readings like sGlobal, sFirmware, sHistory and some settings like holiday and pXX parameters.einige PXX Werte angezeigt werden.
sGlobal (ex allFB)
Contains all actual values like water and gas temperatures, fan states, pressures, ...
sFirmware
Shows the firmware release.
sHistory
Contains information to operating hours, e.g. the compressors operating hours.
pHoliday-Werte
Here you can see the settings of the holiday configuration of the THZ. These are used to override the day setback for the give time. You can change the holiday settings with set.
sLast10errors
Reads the last 10 errors and shows it.
pXX-values & program-values
The pXX & program values are settings like the heating circle, fan states, dhw programs and so on. All pXX and program valueas can be changed with the set command. NEW: Now the fanstage-inlet and outlet volumes are read- and writeable.
pOpMode shows the Operating Mode of the THZ. Like Automatic, Setback, ...
party-time
This parameter sets the party time. While this time range the fan state will change to the in p99FanStageParty stage.
sDHW (ex Status_DHW_F3)
Contains information about the Domestic Hot Water system
sHC1 (ex Status_HC1_F4)
Contains information about the Heatinc Circle 1
sHC2 (ex Status_HC2_F5)
Information of HC2
sSol (ex Status_Sol_16)
Solar Heating System informations
pOpMode (ex OperatingMode) OperatingMode of the heating. One of: Standby, Automatic, DAYmode, SetBack, DHWmode, Manual, Emergency
Plots - graphical views
This shows you how to create plots from the heatpump readings.
Example
Assuming we want to read and plot the outside_temp and the dhw_temp from the sGlobal reading:
Creating the plot in fhem.cfg:
define Plot_Temp SVG FileLog_Mythz:thz:CURRENT
attr Plot_Temp room Heizung
This will setup the plot without any data and maybe with an error message. Klick on the plot-name to open the plot config windows. Here you enter the details.
Most important are now the input fields
Below the input mask you find the according readings to Mythz, including sGlobal.
sGlobal will like like this:
2014-03-02_13:07:49 Mythz sGlobal: outside_temp: 3.8 flow_temp: 26.5 return_temp: 27.2 hot_gas_temp: 32.1 dhw_temp: 43.4 flow_temp_HC2: -60 evaporator_temp: 5.3 condenser_temp: 27.4 Mixer_open: 0 Mixer_closed: 0 HeatPipeValve: 0 DiverterValve: 0 DHW_Pump: 0 .................output omitted
To find the right input value just count the space seperated data. So the value for outside_temp is 5 and dhw_temp is 13 as these are the positions they are on. This number will be entered into the input field to create the plot with the chosen data.
More information to Creating Plots
extract single values from readings
To separate values to from the "big readings" like sGlobal or history you can use a userReading.
Example:
attr Mythz userReadings OutsideTemp {(split ' ',ReadingsVal("Mythz","sGlobal",0))[1]},
FlowTemp {(split ' ',ReadingsVal("Mythz","sGlobal",0))[3]}
More information to userReadings can be found in the CommandRef
Notes
  • A full refresh (of all parameters) is done only at systemstart, very very slowly (not to decrease performance of FHEM), and takes ca 3 or 4 minutes. After that the intervall polling of sGlobal and sHistory register should start.
  • If the FB-intervall or History-Intervall attributes are lower than 3 minutes, there clould be a concurrency. But that shouldn't cause any problems.
known Problems
In the FHEM Log you will find messages like this when using Ser2Net:
2014.03.02 09:41:09 1: 192.168.178.50:2003 disconnected, waiting to reappear
2014.03.02 09:41:09 1: 192.168.178.50:2003 reappeared (Mythz)
This problem is not solved until now.
Release History
v0.067
Module first implemented in FHEM
v0.068
new command for party
v0.069
added German CommandRef
v0.070
BugFix in status bits
v0.071
Bugfix, undefFn improved
v0.072
  • all programHC1*, programHC2*, programFan* and programDHW* have been implemented with get and set
  • inside_temp has been added to the end of allFB
  • connect/disconnet bug related to ser2net has been extremely improved: max one retry per second
v0.074
now the parameters air inlet- outlet-volumes and passive cooling are read and writeable
v0.075
implemented interval_last10errors. Interval for polling the internal fault memory of the heatpump.
v0.076
Bugfixes and new parameter Status_HC1_F4
v0.078
new parameters Status_Sol_16 and Status_DHW_F3
v0.080
  • new Parameters p49SummerModeTemp and p50SummerModeHysteresis
  • Status_HC1_F4 and Status_HC2_F5 now showing "mode: Summer" (or Winter)
Calculation of the mode is:
if outsidetemp > p49SummerModeTemp + p50SummerModeHysteresis ---> Summermode
if outsidetemp < p49SummerModeTemp - p50SummerModeHysteresis ---> Wintermode
v0.081
BugFix for Sommer/Wintermodus-Anzeige
v0.084
  • OperatingMode now displayed (read-only)
  • p33BoosterTimeoutDHW (read/write)
  • p79BoosterTimeoutHC (read/write)
v0.085
OperatingMode is now read/write
v0.087
  • Neue Readings
  • Angepasste Readingnamen
v0.089
  • Improvements on communication
  • Bugfixes
  • New readings
v0.091
New Readings: sHeatRecoveredDay & sHeatRecoveredTotal
Beispielkonfiguration
Start Definition mit Ser2Net
define Mythz THZ 192.168.111.5:2003
attr Mythz room Sysintern
userReadings
attr Mythz userReadings AussenTemp:sGlobal {(split ' ',ReadingsVal("Mythz","sGlobal",0))[1]}, VorlaufTemp:sGlobal {(split ' ',ReadingsVal("Mythz","sGlobal",0))[3]}, RuecklaufTemp:sGlobal {(split ' ',ReadingsVal("Mythz","sGlobal",0))[5]}, WWTemp:sGlobal {(split ' ',ReadingsVal("Mythz","sGlobal",0))[9]}, KollektorTemp:sGlobal {(split ' ',ReadingsVal("Mythz","sGlobal",0))[79]}
interval Defintionen
Definition von file-log und den SVG-Plots einiger Daten
define FileLog_Mythz FileLog ./log/Mythz-%Y-%m.log Mythz
define wal_0 SVG FileLog_Mythz:thz:CURRENT
attr wal_0 room Heizung
define wal_1 SVG FileLog_Mythz:thz1:CURRENT
attr wal_1 room Heizung
define wal_2 SVG FileLog_Mythz:thz2:CURRENT
attr wal_2 room Heizung
define wal_3 SVG FileLog_Mythz:thz3:CURRENT
attr wal_3 room Heizung
define wal_4 SVG FileLog_Mythz:thz4:CURRENT
attr wal_4 room Heizung
readingsGroup
define rg_thz readingsGroup Mythz:<%temp_outside>,<Aussen>,AussenTemp Mythz:<%sani_supply_temp@red>,<Vorlauf>,VorlaufTemp Mythz:<%sani_return_temp@blue>,<Rücklauf>,RuecklaufTemp Mythz:<%sani_boiler_temp@BD7800>,<Wasser>,WWTemp Mythz:<%sani_solar_temp>,<Kollektor>,KollektorTemp
attr rg_thz alias Heizung Temperaturen
attr rg_thz group THZ
attr rg_thz room Sysintern
attr rg_thz valueFormat { AussenTemp => '%1.f °C', VorlaufTemp => '%1.f °C', AussenTemp=> '%1.f °C', RuecklaufTemp=> '%1.f °C', WWTemp=> '%1.f °C', KollektorTemp=> '%1.f °C' }
Dashboard
define MyDashboard Dashboard
attr MyDashboard dashboard_lockstate unlock
attr MyDashboard dashboard_row top-center
attr MyDashboard dashboard_showhelper 0
attr MyDashboard dashboard_showtooglebuttons 0
attr MyDashboard dashboard_tab1groups THZ
attr MyDashboard dashboard_tab1name micofhem
attr MyDashboard dashboard_tab1sorting t0c100,THZ,true,170,253
attr MyDashboard dashboard_tabcount 1
attr MyDashboard dashboard_webfrontendfilter WEB
define MyDashboard_weblink weblink htmlCode {DashboardAsHtml("MyDashboard")}
attr MyDashboard_weblink room DashboardRoom
FanSelector für die Lüftungssteuerung
define FanSelectorDay dummy
attr FanSelectorDay group THZ
attr FanSelectorDay setList 0 1 2 3 offFor60min
attr FanSelectorDay webCmd 0:1:2:3:offFor60min
attr FanSelectorDay devStateIcon 0:vent_ventilation_level_0 1:vent_ventilation_level_1 2:vent_ventilation_level_2 3:vent_ventilation_level_3
define Notify_p07FanStageDay notify FanSelectorDay IF ([FanSelectorDay] eq "offFor60min") (define at_D_offFor60min at +00:59:00 set Mythz p07FanStageDay [Mythz:p07FanStageDay],set Mythz p07FanStageDay 0, setstate FanSelectorDay offFor60min) ELSE (set Mythz p07FanStageDay $EVENT)
define Notify_FanselectorDay notify (Mythz.p07FanStageDay.*) setstate FanSelectorDay $EVTPART1
attr FanSelectorDay room heatpump
define FanSelectorNight dummy
attr FanSelectorNight group THZ
attr FanSelectorNight setList 0 1 2 3 offFor60min
attr FanSelectorNight webCmd 0:1:2:3:offFor60min
attr FanSelectorNight devStateIcon 0:vent_ventilation_level_0 1:vent_ventilation_level_1 2:vent_ventilation_level_2 3:vent_ventilation_level_3
define Notify_p08FanStageNight notify FanSelectorNight IF ([FanSelectorNight] eq "offFor60min") (define at_N_offFor60min at +00:59:00 set Mythz p08FanStageNight [Mythz:p08FanStageNight],set Mythz p08FanStageNight 0, setstate FanSelectorNight offFor60min) ELSE (set Mythz p08FanStageNight $EVENT)
define Notify_FanselectorNight notify (Mythz.p08FanStageNight.*) setstate FanSelectorNight $EVTPART1
attr FanSelectorNight room heatpump
Launchpad Heatpumpmonitor
Thread in the FHEM-Forum